Multiple Choice
One transfer switch shall be permitted to serve one or more branches or systems in a facility with a continuous load on the switch of ____ or less.
A) 100 kVA
B) 110 kVA
C) 125 kVA
D) 150 kVA
Correct Answer:

Verified
Correct Answer: