Multiple Choice
The allowable ampacity of a 4 AWG THHN conductor is 95 amperes.If we have four 4 AWG THHN conductors, what is the adjusted ampacity?
A) 48
B) 63
C) 76
D) 95
Correct Answer:

Verified
Correct Answer:
Verified