True/False
While troubleshooting a 24-V control circuit consisting of a thermostat, a pressure control, and a contactor coil, the technician reads 24 volts across the thermostat, 0 volts across the pressure control, and 0 volts across the contactor coil. The technician makes the following statements. The following statements are all considered to be true.
A) The transformer is burned out.
B) The thermostat is open.
C) The contactor coil is energized.
Correct Answer:

Verified
Correct Answer:
Verified
Q6: The cooling anticipator in a thermostat is
Q7: Without _ voltage, there is no low
Q8: In a high voltage circuit, is the
Q9: Explain how to read very low currents
Q10: The heat anticipator in a thermostat is
Q12: Electrical controls are divided into two categories:
Q13: A control can be which of the
Q14: A 10-wrap amperage multiplier is used with
Q15: How is the heat anticipator normally wired
Q16: How is the cooling anticipator normally wired