    In a 2-Ton TX Valve System, the Unit Does Not
Solved

In a 2-Ton TX Valve System, the Unit Does Not

Question 29

Question 29

Short Answer

In a 2-ton TX valve system, the unit does not develop full capacity. Head pressure is high, suction pressure is slightly above normal, superheat is normal, and subcooling is above normal. What is the problem?

Correct Answer:

verifed

Verified

The proble...

View Answer

Unlock this answer now
Get Access to more Verified Answers free of charge

Related Questions

Q24: The water quality required to maintain the

Q25: In a wastewater system, the water entering

Q26: With the entering air to the condenser

Q27: The refrigerated cabinet temperature of a high-temperature

Q28: In a wastewater system, the water entering

Q30: A sight glass that is full of

Q31: In a water-cooled condensing unit/cooling tower combination,

Q32: Bubbles in the sight glass always indicate

Q33: If the evaporator and compressor are starved

Q34: Condensing units located outside that are required

Examlex

ExamLex

About UsContact UsPerks CenterHomeschoolingTest Prep

Work With Us

Campus RepresentativeInfluencers

Links

FaqPricingChrome Extension

Download The App

Get App StoreGet Google Play

Policies

Privacy PolicyTerms of ServiceHonor CodeCommunity Guidelines

Scan To Download

qr-code

Copyright © (2025) ExamLex LLC.

Privacy PolicyTerms Of ServiceHonor CodeCommunity Guidelines